In my hypothetical case, with R = 0.2 ohms, current will go up to of order 1000A (not quite that high, due to combined R and l, but near enough).
And there is nothing to stop having higher voltages driving a higher R coil.
I
If the coil is directly connected to the mains voltage if the scr is on, then the mains has to supply this current.
Standard 3 phase industrial connections are rated for about 35 Amps RMS per phase in Europe. I doubt if they can supply 1000 Amp, even for short moments
If an intermediate transformer is used, then since the currents are measured on the supply side, the measured current would have been lower with a factor equal to the turn ratio.
Thus i still find it very unlikely that those large currents would be flowing.
Also we have the SCR controller.
The type of scr controller used can be bougth in several versions, with different amparage rating. The maximum value being 160 Amp for the type used.
The controller has an internal overcurrent trip point of 175% of this rated value, thus 280 Amp. If it goes beyond that 280 Amp, the SCR controller shuts down.
Thus I find it very unlikely if we ever would see currents above that value.